I would like to know where in the regs it says we have to fit an SPD. As far as i am aware the advise given was we should offer it to the customer and it was up to them , it is not a condition of a compliant 18th edition install.
18th reg 443.4 demands that protection against transient overvoltages shall be provided unless the risk assessment (443.5) shows it's not required or (for single dwelling units only) the total value of the installation and equipment therein does not justify such protection.
The risk assessment tends to say SPDs are needed unless you're in a city-centre kind of environment, but the details vary.
The ‘value of the installation and equipment therein does not justify such protection’ option is a bit vague, some guidance has suggested that 5x the cost of the SPDs would be the limit - which would be hard to justify in the modern home (the cost of a TV and washing machine alone would probably put you above that line).
(As an aside, putting SPDs on the mains alone, while leaving say the phone line and TV aerial unprotected, might not entirely provide adequate protection, which might be something to factor into the cost calculation.)
- Andy.
I would like to know where in the regs it says we have to fit an SPD. As far as i am aware the advise given was we should offer it to the customer and it was up to them , it is not a condition of a compliant 18th edition install.
18th reg 443.4 demands that protection against transient overvoltages shall be provided unless the risk assessment (443.5) shows it's not required or (for single dwelling units only) the total value of the installation and equipment therein does not justify such protection.
The risk assessment tends to say SPDs are needed unless you're in a city-centre kind of environment, but the details vary.
The ‘value of the installation and equipment therein does not justify such protection’ option is a bit vague, some guidance has suggested that 5x the cost of the SPDs would be the limit - which would be hard to justify in the modern home (the cost of a TV and washing machine alone would probably put you above that line).
(As an aside, putting SPDs on the mains alone, while leaving say the phone line and TV aerial unprotected, might not entirely provide adequate protection, which might be something to factor into the cost calculation.)
- Andy.