Anybody able to explain the difference to me as I hear both terms used?
  • I see centre-tapped maybe the difference with this being a safety isolating.

  • Whereas 0-110V is simply isolating?


And when and where would an application suit either? Normally these days all control panel transformers are 0-110Vac for control although quite often when you debug older panels you will see Centre Tapped ones?
Parents
  • I think the same applies as I posted on another thread regarding earthing the 0V of a 24Vdc power supply, where a single fault on a centre tapped transformer can leave a voltage where it should not be. Therefore with regards control its always in my experience not correct to use centre tapped. 


    I found this on another thread:


    EN 60204-1 clause 9.4.3 would apply in this case.

    There are 3 methods, one is a conventional "TN-S" supply where the 0V / d.c. - ve is tied to earth.

    The second is an unearthed system with earth fault monitoring.

    The third is a CTE system.

    However, whichever one of these is used the overriding statement is:

    "9.4.3.1 Earth faults

    Earth faults on any control circuit shall not cause unintentional starting, potentially hazardous

    motions, or prevent stopping of the machine."

    There is a note to the use of a CTE supply:

    "NOTE 1 On a centre-tapped earthed control circuit, the presence of one earth fault can leave 50 % voltage on a relay coil. In this condition, a relay can hold on, resulting in inability to stop a machine."

    Thus, there is the possibility of a CTE supply allowing an earth fault which can cause danger and thus be in contravention of 9.4.3.1.
Reply
  • I think the same applies as I posted on another thread regarding earthing the 0V of a 24Vdc power supply, where a single fault on a centre tapped transformer can leave a voltage where it should not be. Therefore with regards control its always in my experience not correct to use centre tapped. 


    I found this on another thread:


    EN 60204-1 clause 9.4.3 would apply in this case.

    There are 3 methods, one is a conventional "TN-S" supply where the 0V / d.c. - ve is tied to earth.

    The second is an unearthed system with earth fault monitoring.

    The third is a CTE system.

    However, whichever one of these is used the overriding statement is:

    "9.4.3.1 Earth faults

    Earth faults on any control circuit shall not cause unintentional starting, potentially hazardous

    motions, or prevent stopping of the machine."

    There is a note to the use of a CTE supply:

    "NOTE 1 On a centre-tapped earthed control circuit, the presence of one earth fault can leave 50 % voltage on a relay coil. In this condition, a relay can hold on, resulting in inability to stop a machine."

    Thus, there is the possibility of a CTE supply allowing an earth fault which can cause danger and thus be in contravention of 9.4.3.1.