High 3rd harmonic on the neutral

Afternoon,

I was wondering if anyone has nay experiences of having issues with high 3rd harmonic currents on the neutral on high-rised residential schemes? I appreciate  non-linear single phase loads will impact the 3rd harmonic and even on a balanced system harmonics are an issue but we are measuring it at 300% but I can’t think why this may be the case on a residential building.

Does anyone have any ideas?



M
Parents
  • Those figures are not possible. If all 3 phases are taking 100A there will be zero neutral current. The vector difference of 50A says that they are not all similar. What are you testing with?
Reply
  • Those figures are not possible. If all 3 phases are taking 100A there will be zero neutral current. The vector difference of 50A says that they are not all similar. What are you testing with?