Chris Pearson:John Peckham:
It can't be that big a block of flats at 100A a phase?
MS01:
My thought was this is a big block of flats 300+ which are used by students and now with lectures online mostly will be using laptops....what are peoples thoughts?I did wonder: that's 1 amp per flat.
In fact if they are centrally heated bed-sits with a shower and WC, and no kettles, etc. allowed, they probably would get by with 230 W (after diversity).
1 amp per flat is in my view possible at times of low load, That does not mean that a 100 amp 3 phase supply is enough for 300 flats, the load could easily average 5 amps or more per flat at peak times. But an average of 1 amp at times sounds reasonable.
Chris Pearson:John Peckham:
It can't be that big a block of flats at 100A a phase?
MS01:
My thought was this is a big block of flats 300+ which are used by students and now with lectures online mostly will be using laptops....what are peoples thoughts?I did wonder: that's 1 amp per flat.
In fact if they are centrally heated bed-sits with a shower and WC, and no kettles, etc. allowed, they probably would get by with 230 W (after diversity).
1 amp per flat is in my view possible at times of low load, That does not mean that a 100 amp 3 phase supply is enough for 300 flats, the load could easily average 5 amps or more per flat at peak times. But an average of 1 amp at times sounds reasonable.