Chris Pearson:John Peckham:
It can't be that big a block of flats at 100A a phase?
MS01:
My thought was this is a big block of flats 300+ which are used by students and now with lectures online mostly will be using laptops....what are peoples thoughts?I did wonder: that's 1 amp per flat.
In fact if they are centrally heated bed-sits with a shower and WC, and no kettles, etc. allowed, they probably would get by with 230 W (after diversity).
1 amp per flat is in my view possible at times of low load, That does not mean that a 100 amp 3 phase supply is enough for 300 flats, the load could easily average 5 amps or more per flat at peak times. But an average of 1 amp at times sounds reasonable.
MS01:
The highest phase it at just over 100A with the other phases there or there abouts but the neutral current is at 50A
How do you achieve balancing a three phase load in a residential building with single phase loads that will cancel the neutral current?
You can balance the load to get an even load across the phases, but you cannot cancel the neutral can you?
It’s over twenty years since I sat drawing diagrams during evening classes at Kidderminster College, but I don’t remember one where it showed how a single phase neutral current is cancelled.
Andy Betteridge
broadgage:Chris Pearson:John Peckham:
It can't be that big a block of flats at 100A a phase?
MS01:
My thought was this is a big block of flats 300+ which are used by students and now with lectures online mostly will be using laptops....what are peoples thoughts?I did wonder: that's 1 amp per flat.
In fact if they are centrally heated bed-sits with a shower and WC, and no kettles, etc. allowed, they probably would get by with 230 W (after diversity).1 amp per flat is in my view possible at times of low load, That does not mean that a 100 amp 3 phase supply is enough for 300 flats, the load could easily average 5 amps or more per flat at peak times. But an average of 1 amp at times sounds reasonable.
We haven't been told the capacity of the supply, just that the currents in the phases are about 100 A each.
MS01:
My thought was this is a big block of flats 300+ which are used by students and now with lectures online mostly will be using laptops....what are peoples thoughts?
We are doing some load montitoring and we noticed this issues.
So does each flat have an independent installation with a consumer unit in each supplied from a three phase distribution board that does not have any three phase loads connected into it at all?
Andy B.