Or a PHASE CURRENT & LINE CURRENT result of 7.53A if 3000W is entered (which I understand would be the Wattage per phase)
How did you manage to come up with that figure? 3000 / 230 = 13.04. (Which is why we have 13A sockets in the UK). A 9000W wye element is really just three 3000W single phase elements, one per phase.
Or a PHASE CURRENT & LINE CURRENT result of 7.53A if 3000W is entered (which I understand would be the Wattage per phase)
How did you manage to come up with that figure? 3000 / 230 = 13.04. (Which is why we have 13A sockets in the UK). A 9000W wye element is really just three 3000W single phase elements, one per phase.