MCB & Cable Size for 3 Phase Star (Wye) with Neutral

Hi, I'm trying to understand/figure out what MCB & Cable Size would be required for a 3 Phase 9kW Immersion Element wired in Star using Neutral?  I have been a little confused by the results when using various online calculators. One example here: https://www.watlow.com/resources-and-support/engineering-tools/3phase-delta-wye-calculator

i.e. Using a Line Voltage of 400V equals a Phase & Line Current of 12.99A.  Where as using a Phase Voltage of 230V equals a Phase & Line Current of 22.59A?


My questions are:

1. Are these calculations correct?

2. What Amperage MCB would be required?

3. Would the MCB required need to be 3P, 3P+N or 4P?

3. Would 1.5mm2 cable at a 6 meter run be adequate?


Thanks in advance for your feedback and help.
Parents
  • Former Community Member
    0 Former Community Member
    If you use convenient calculation tools, the task is very simple.

    Load = 3 Phase Immersion Element
    P = 9kW
    Line voltage (phase-phase) = 400V
    Cos phi = 1.0
    Phase current = 12.99 A
    72fbda1d0ca232491d8e079665dcd319-original-meteorspec1.png



    The current carrying capacity depends on the installation conditions.

    d36e50d772f9cf31573f42dc2ca9ce69-original-meteorspec2.png

    Cable selected = Cu 2.5mm2  3p+N, 

    Protection = MCB 3x16A


    and calculation report:
    9ada74f9820e035a90fdafce5dd77c48-original-meteorspec3.png





Reply
  • Former Community Member
    0 Former Community Member
    If you use convenient calculation tools, the task is very simple.

    Load = 3 Phase Immersion Element
    P = 9kW
    Line voltage (phase-phase) = 400V
    Cos phi = 1.0
    Phase current = 12.99 A
    72fbda1d0ca232491d8e079665dcd319-original-meteorspec1.png



    The current carrying capacity depends on the installation conditions.

    d36e50d772f9cf31573f42dc2ca9ce69-original-meteorspec2.png

    Cable selected = Cu 2.5mm2  3p+N, 

    Protection = MCB 3x16A


    and calculation report:
    9ada74f9820e035a90fdafce5dd77c48-original-meteorspec3.png