ADS
How exactly does ADS work?
  • Hi, can you give more info about what you mean by ADS?
    BS 7671 : 2018 Chapter 41
    411 Protective measure: (A)utomatic (D)isconnection of (S)upply.
  • It's probably best to do a quick google search on the term automatic disconnection of supply ... you'll find a lot of information on the web, and some YouTube videos, that will give you a good idea of what's going on. There's a wealth of information out there. Search link below:
    https://www.google.com/search?q=automatic+disconnection+of+supply
    Then, post back with specific questions and points you are unsure of, and I'm sure the Forum will be pleased to help.
    No one on the web is simply explaining how ADS works!
  • Tell us what part(s) of ADS you don't understand then we can better help you.
  • Coby:
    OK, are you happy with how a fuse or circuit breaker works? The concept that too much current flowing in a circuit causes the fuse or circuit breaker to operate?
  • Well, just for starters...
    ADS is one of several different methods of providing some protection against electric shock under fault conditions, and works by limiting the duration of the shock current. ADS considers metallic parts that would normally be safe to touch but would made hazardous live by a failure of basic insulation - for example the metal cases of electrical equipment. These parts are normally connected to Earth and also the source of the supply is also connected to Earth - such that if a fault does make that part live then a short-circuit is created and protective devices can then detect the short circuit and automatically disconnect the circuit - so removing the hazard. Depending on the details of the Earthing arrangement the protective device might be a simple fuse or a circuit breaker, or might need to be a residual current device.
    How about if I tell you what I do understand?
    When I employ EEBADS I know that every conductive part within a building (that is immovable and/or can be gripped by a human hand) will be at the same potential, therefore if any 'hazardous live' line conductor comes into contact with any conductive part within the building, I can predict an automatic disconnection time not exceeding 0.4 seconds.
    Therefore; no immovable conductive parts or conductive parts that can be gripped by the human hand, can remain hazardous live for more than 0.4 seconds.
    So if you've taken away the "earthed equipotential bonding" element, how does "automatic disconnection of supply" actually work?
  • Coby:
    OK, that's not quite correct.
    The automatic disconnection time is calculated just from the earth fault path of the circuit concerned, without considering earthed equipotential bonding, using the formula:
    Zs = Ze + (R1+R2)
    Where:
    Zs the total earth fault loop impedance
    Ze is the external earth fault loop impedance to the origin of the installation (the DNO network)
    R1 is the resistance of the line conductor of the circuit (at 70 degrees)
    R2 is the resistance of the protective conductor of the circuit (at 70 degrees)
    Compare Zs with the relevant Table in Chapter 41 of BS 7671 for the protective device concerned, to make sure you can achieve the disconnection time (usually 0.4 s for installations with TN-C-S or TN-S earthing arrangement, 0.2 s for installations with TT earthing arrangement)
    So, what does earthed equipotential bonding do?
    When a fault occurs, the point of fault rises in voltage. The voltage rise is due to Ohms Law, and depends on the fault current flowing, and the resistance of the protective conductor path. It could be anywhere up to the full line to neutral voltage of the system (230 V), if the resistance in the earth path is very large compared to the resistance of the line conductors. The voltage is usually greater in TT systems than TN-S or TN-C-S systems. The voltage will last for the duration of the fault (0.4 s in most circuits in installations with TN-C-S or TN-S earthing arrangement, 0.2 s in most circuits in installations with TT earthing arrangement).
    If a metal pipe comes into the premises from outdoors, this pipe will be at the same potential as the neutral of the supply transformer.
    We use equipotential bonding to help reduce the touch voltage between the metal parts of the equipment with a fault, and the metal pipes from outdoors, for the duration of the fault (0.4 s in most circuits in installations with TN-C-S or TN-S earthing arrangement, 0.2 s in most circuits in installations with TT earthing arrangement). SO, really equipotential bonding has nothing to do with the circuit, but metal parts connected outside the installation.
    Equipotential bonding does not make the touch voltage zero, but often:
     - it will be much lower, inside houses with TT earthing arrangements, than inside houses with TN-S or TN-C-S earthing arrangements
     - It will be much higher outside houses (in the garden) with TT earthing arrangements, than outside houses with TN-S or TN-C-S earthing arrangements.
  • When I employ EEBADS I know that every conductive part within a building (that is immovable and/or can be gripped by a human hand) will be at the same potential, therefore if any 'hazardous live' line conductor comes into contact with any conductive part within the building, I can predict an automatic disconnection time not exceeding 0.4 seconds.
    That's a bit of an over-generalization, but I'll come back to that in a moment...
    Nothing's been taken away. The new name of ADS means the same as the old EEBADS.
    By way of explanation, consider that not all metallic parts are thought of in the same way - there are exposed-conductive-parts that are Earthed (not bonded) and extraneous-conductive-parts that are bonded (not earthed).
    For ADS to work, exposed-conductive-parts (metalic cases of electrical equipment) need to be Earthed - no change there.
    Extranous-conducitve-parts (typically water pipes, gas pipes, structural steel) would often be bonded - but not always (not for installations outside of buildings for example) - so the ADS part doesn't rely on bonding of extraneous-conductive-parts for ADS to work - it never has. Bonding has an advantage of reducing touch voltages while ADS operates - and is still required within buildings etc but not in every situation) so ADS is really a better description than EEBADS.
    BTW ADS isn't always required to disconnect within 0.4s - for distribution circuits and larger final circuits 5s is permitted - and for TT systems the equivalent numbers are 0,2s and 1s. Bonding extraneous-conductive-parts is especially helpful with the longer disconnection times,
       - Andy,