wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
That creates more issues than it resolves.
Insert a 300 mA RCD in a plastic enclosure in the tails downstream of the DNO isolation switch and lose the DNO earth terminal, if you cannot easily access the conductor at the intake end take the bar off and put some heat shrink over the end of the conductor.
The earth terminal is the only part of the DNO installation that is exposed and likely to be a risk, it's better off out of there.
wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
That creates more issues than it resolves.
Insert a 300 mA RCD in a plastic enclosure in the tails downstream of the DNO isolation switch and lose the DNO earth terminal, if you cannot easily access the conductor at the intake end take the bar off and put some heat shrink over the end of the conductor.
The earth terminal is the only part of the DNO installation that is exposed and likely to be a risk, it's better off out of there.