wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
DNO earthing is unused.
Armour of SWA cable is currently connected at both ends i believe, but earthed via the earth rod at the load end.
wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
DNO earthing is unused.
Armour of SWA cable is currently connected at both ends i believe, but earthed via the earth rod at the load end.