Chris Pearson:
I see no reason to earth the cabinet, but that switch fuse definitely needs to be earthed. Achieving that via 100 m of SWA and an earth rod seems very odd. In the absence of an RCD it is definitely no better than C2.
What size fuses are in the switch fuse and what is the EFLI at the DB?
Not sure what's in side the fused isolator yet but agree it needs earthed as it stands and with a upfront RCD, my own thought was to replace it with a plastic enclosure and a MCB & RCD (100mA Time delay) within, as the fuse isolator has been noted to be potentially faulty anyway.
The earth fault loop impedance is way too high for anything currently protecting the cable i think my MFT recorded around 10ohm / 25A, but it had been raining a while so the ground was soaked so this was probably best case, but generally speaking i thought it was a good low TT reading.
Chris Pearson:
I see no reason to earth the cabinet, but that switch fuse definitely needs to be earthed. Achieving that via 100 m of SWA and an earth rod seems very odd. In the absence of an RCD it is definitely no better than C2.
What size fuses are in the switch fuse and what is the EFLI at the DB?
Not sure what's in side the fused isolator yet but agree it needs earthed as it stands and with a upfront RCD, my own thought was to replace it with a plastic enclosure and a MCB & RCD (100mA Time delay) within, as the fuse isolator has been noted to be potentially faulty anyway.
The earth fault loop impedance is way too high for anything currently protecting the cable i think my MFT recorded around 10ohm / 25A, but it had been raining a while so the ground was soaked so this was probably best case, but generally speaking i thought it was a good low TT reading.