Steve UKBC:Chris Pearson:
What size fuses are in the switch fuse and what is the EFLI at the DB?The earth fault loop impedance is way too high for anything currently protecting the cable i think my MFT recorded around 10ohm / 25A, but it had been raining a while so the ground was soaked so this was probably best case, but generally speaking i thought it was a good low TT reading.
Sorry, that's not really what I meant to ask. What is Ze, and what is R1+R2 of the distribution circuit.
If you don't know what size fuses are in there, how do know "The feeder cable to DB1 some +100m away has not got a low enough impedance to clear a earth fault with the 100A DNO fuses/fused isolator within 5s required by BS7671 ..."
Steve UKBC:Chris Pearson:
What size fuses are in the switch fuse and what is the EFLI at the DB?The earth fault loop impedance is way too high for anything currently protecting the cable i think my MFT recorded around 10ohm / 25A, but it had been raining a while so the ground was soaked so this was probably best case, but generally speaking i thought it was a good low TT reading.
Sorry, that's not really what I meant to ask. What is Ze, and what is R1+R2 of the distribution circuit.
If you don't know what size fuses are in there, how do know "The feeder cable to DB1 some +100m away has not got a low enough impedance to clear a earth fault with the 100A DNO fuses/fused isolator within 5s required by BS7671 ..."