Sparkingchip:
So you are making the SWA feeder circuit TT after all.
That's a set up that neither Andy J or myself had in mind ?
Id prefer not to take the PME earth to the farm buildings and keep the TT/PME switch away from the area and in the cabinet in the field adjacent to the TX pole, as you cannot know the future use or these farm buildings, there is currently no livestock but who's to say this does not change in the near future.
Any outer damage of the feeder cable if the PME earth were to be brought to the farm building (i.e exposed SWA carrying the PME earth) would introduce the PME earth potentially closer to the farm building earth electrodes would it not?
Sparkingchip:
So you are making the SWA feeder circuit TT after all.
That's a set up that neither Andy J or myself had in mind ?
Id prefer not to take the PME earth to the farm buildings and keep the TT/PME switch away from the area and in the cabinet in the field adjacent to the TX pole, as you cannot know the future use or these farm buildings, there is currently no livestock but who's to say this does not change in the near future.
Any outer damage of the feeder cable if the PME earth were to be brought to the farm building (i.e exposed SWA carrying the PME earth) would introduce the PME earth potentially closer to the farm building earth electrodes would it not?