AJJewsbury:I know I'm probably going to get comments on the 100A MCB following the 100A fuses and I'm open to these comments as I know the selectivity lines cross between these two devices
I wouldn't be particularly worried about discrimination between the DNO's fuses and your up-front overcurrent protection - everything goes off either way - there's no additional loss of service as it were if the DNO's go first (or as well). There's just the inconvenience of having to get the DNO to replace the fuses rather than your local electrician (but the cable will probably need fixing first either way).
I would be concerned about lack of discrimination between your up-front overcurrent protection and downstream MCBs (or RCBOs) - in practice there's simply no guaranteed discrimination between MCBs regardless of their ratings. Unlike fuses where having an upstream device rated 2x (or 1.6x) the rating of the downstream one will usually provide discrimination, there's no such relationship between MCBs. If the fault current is high enough both MCBs will see the fault, and both will de-latch before either have fully opened.
- Andy.
Andy, there is only so much we can do to mitigate these issues, selectivity studies have been carried out to ensure best practice and to limit multiple devices de-latching/tripping on a fault.
AJJewsbury:I know I'm probably going to get comments on the 100A MCB following the 100A fuses and I'm open to these comments as I know the selectivity lines cross between these two devices
I wouldn't be particularly worried about discrimination between the DNO's fuses and your up-front overcurrent protection - everything goes off either way - there's no additional loss of service as it were if the DNO's go first (or as well). There's just the inconvenience of having to get the DNO to replace the fuses rather than your local electrician (but the cable will probably need fixing first either way).
I would be concerned about lack of discrimination between your up-front overcurrent protection and downstream MCBs (or RCBOs) - in practice there's simply no guaranteed discrimination between MCBs regardless of their ratings. Unlike fuses where having an upstream device rated 2x (or 1.6x) the rating of the downstream one will usually provide discrimination, there's no such relationship between MCBs. If the fault current is high enough both MCBs will see the fault, and both will de-latch before either have fully opened.
- Andy.
Andy, there is only so much we can do to mitigate these issues, selectivity studies have been carried out to ensure best practice and to limit multiple devices de-latching/tripping on a fault.