Steve UKBC:
(originally)
So we are left with a metal cabinet where the PME supply switches over to a TT.
(later)
Id prefer not to take the PME earth to the farm buildings and keep the TT/PME switch away from the area and in the cabinet in the field adjacent to the TX pole, as you cannot know the future use or these farm buildings, there is currently no livestock but who's to say this does not change in the near future.Any outer damage of the feeder cable if the PME earth were to be brought to the farm building (i.e exposed SWA carrying the PME earth) would introduce the PME earth potentially closer to the farm building earth electrodes would it not?
I don't think it is at all correct to say that the PME supply switches over to TT. The distributor's earth is simply sitting there unused.
If DB1 is in a farm building which has potential for housing livestock, I can understand the reluctance to take the PME supply to it, but as things stand you have exposed conducting parts of two earthing systems which are very obviously simultaneously accessible contrary to 411.3.1.1 On reflection, I may upgrade to C1!
Get rid of that shoelace of an earthing conductor between the service head and "MET" and preferably, bung in another earth rod near the origin.
Steve UKBC:
(originally)
So we are left with a metal cabinet where the PME supply switches over to a TT.
(later)
Id prefer not to take the PME earth to the farm buildings and keep the TT/PME switch away from the area and in the cabinet in the field adjacent to the TX pole, as you cannot know the future use or these farm buildings, there is currently no livestock but who's to say this does not change in the near future.Any outer damage of the feeder cable if the PME earth were to be brought to the farm building (i.e exposed SWA carrying the PME earth) would introduce the PME earth potentially closer to the farm building earth electrodes would it not?
I don't think it is at all correct to say that the PME supply switches over to TT. The distributor's earth is simply sitting there unused.
If DB1 is in a farm building which has potential for housing livestock, I can understand the reluctance to take the PME supply to it, but as things stand you have exposed conducting parts of two earthing systems which are very obviously simultaneously accessible contrary to 411.3.1.1 On reflection, I may upgrade to C1!
Get rid of that shoelace of an earthing conductor between the service head and "MET" and preferably, bung in another earth rod near the origin.