AJJewsbury:AJJewsbury:RCD in the DNO cabinet would be the better solution since the clearance time for a earth fault may be above 5s
Provided everything is OK for voltage drop and R2 isn't massively larger than R1, I would be surprised if you couldn't get 5s disconnection times from the usual overcurrent protective devices.
- Andy.Come to that what is your voltage drop like? 100m is quite long for a LV submain and your diagram seems to suggest it's just 35mm² - on what's presumably something close to a 100A/phase system? While the tabulated v.d. of 1.1mV/A/m will be an over estimate as you'll be running the cable a bit cooler than 70 degrees there doesn't feel to be much scope for achieving the usual 3% overall for downstream lighting circuits - even an overall 5% to the end of final circuits looks rather tight (even if you claim the extra 0.005%/m beyond 100m).
- Andy.
Hi Andy,
As previously stated, the feeder cable cannot change and the volt drop has always been a concern (especially lighting), But my calcs have provided confidence that the volt drop is within the limits, some oversized cables down the line have been used purely for the volt drop.
A load assessment and final circuit voltage readings are to be recorded on completion for this very fact.
AJJewsbury:AJJewsbury:RCD in the DNO cabinet would be the better solution since the clearance time for a earth fault may be above 5s
Provided everything is OK for voltage drop and R2 isn't massively larger than R1, I would be surprised if you couldn't get 5s disconnection times from the usual overcurrent protective devices.
- Andy.Come to that what is your voltage drop like? 100m is quite long for a LV submain and your diagram seems to suggest it's just 35mm² - on what's presumably something close to a 100A/phase system? While the tabulated v.d. of 1.1mV/A/m will be an over estimate as you'll be running the cable a bit cooler than 70 degrees there doesn't feel to be much scope for achieving the usual 3% overall for downstream lighting circuits - even an overall 5% to the end of final circuits looks rather tight (even if you claim the extra 0.005%/m beyond 100m).
- Andy.
Hi Andy,
As previously stated, the feeder cable cannot change and the volt drop has always been a concern (especially lighting), But my calcs have provided confidence that the volt drop is within the limits, some oversized cables down the line have been used purely for the volt drop.
A load assessment and final circuit voltage readings are to be recorded on completion for this very fact.