Sparkingchip:wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
That creates more issues than it resolves.
Insert a 300 mA RCD in a plastic enclosure in the tails downstream of the DNO isolation switch and lose the DNO earth terminal, if you cannot easily access the conductor at the intake end take the bar off and put some heat shrink over the end of the conductor.
The earth terminal is the only part of the DNO installation that is exposed and likely to be a risk, it's better off out of there.
The earth terminal is the only part of the DNO installation that is exposed and likely to be a risk, it's better off out of there. >>>>>> would this be by providing a barrier or asking the DNO to come out and remove it?
AJJewsbury:RCD in the DNO cabinet would be the better solution since the clearance time for a earth fault may be above 5s
Provided everything is OK for voltage drop and R2 isn't massively larger than R1, I would be surprised if you couldn't get 5s disconnection times from the usual overcurrent protective devices.
- Andy.
Agree the RCD would be the better solution.
Re volt drop the initial calc was based on the DNO fuses only (as i didn't know what was installed in the fused isolator) and based on this (although wrongly) the disconnection time was over 5s. The volt drop for the whole installation is a concern particularly for the first 100m due to the new expected loads etc. but the cables further down the distribution are being selected to keep the volt drop within the regulations of 3-3.5% lighting and 5-5.5% power (length depending)
Sparkingchip:
Just because there is an earth connection supplied by the DNO you don't have to use it and if you do it your decision to make.
It is the only TNCS earthed item in the whole TT installation, if you are kneeling on the wet ground and lean against the metal cabinet you could feel a tingle if you touch the DNO earth terminal or possibly a bit more. It's not lethal as in if you touch you will die, but it serves no purpose and could be a risk.
Enclose it in a plastic box or something if you think someone may decide it could be required in the future, it doesn't need to be complicated.
The RCD is not the better solution, it is the only solution. Unless you are going to take the TNCS-PME earth connection to where it does not need to be.
Agreed the RCD is the best option but would the alternative solution not be to take the PME earth to an insulated enclosure just before DB1 (change over to TT) as long as the disconnection times are within 5s with the protection within the fused isolator?
The RCD is not the better solution, it is the only solution