wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
That creates more issues than it resolves.
Insert a 300 mA RCD in a plastic enclosure in the tails downstream of the DNO isolation switch and lose the DNO earth terminal, if you cannot easily access the conductor at the intake end take the bar off and put some heat shrink over the end of the conductor.
The earth terminal is the only part of the DNO installation that is exposed and likely to be a risk, it's better off out of there.
Sparkingchip:
And I would not rush to connect the cabinet to the DNO earth bar, but would connect it to the Crabtree Fusestar earth bar.
I am not seeing any reason to replace the Crabtree Fusestar, insert the RCD in the tails and connect the cabinet to the fused switch earth bar seems to be all that is required. Removing the DNO main earth conductor from the intake seems like a good idea, it's of no use and is a hazard to be avoided by anyone working in the cabinet.
Just realised what the quote button is for on here doh.
Its been suggested that the crabtree unit is faulty, but have not confirmed this myself yet. Also space may be a bit tight for a enclosed RCD in addition to the fusestar unit without jiggling things about.
UKPN suggested the cabinet should not be bonded outside of the equipotential zone or for wiring regulations?
mapj1:
Ah - a picture speaks 1k words . Not my mental picture at all.
Leave the outer enclosure street box as it is - the DNO kit is in effect double insulated or reinforced insulation, and no further action needed on that score.
I'm with Andy B above. Ignore the company earth terminal altogether but get an RCD in there - it can be a high current one assuming the TT earth is good enough.
A 300mA ordinary one will detect cable faults between it and the destination, and will not be pushed off balance by anything much less than 100mA of DC - this sadly is not a parameter written in the specs, but given the way magnetic cores operate, is undoubtedly true. Closer protection can be afforded at the load end. Something like the second label might be a good remineder (these are Irish but a UK variant must exist.)
Was thinking a type S (time delay) 100mA type A RCD with 30mA RCBO's on all final circuits to prevent multiple RCD's tripping on a fault, are you suggesting 300mA (non time delayed?) up front and 30mA RCBO's on the final circuits may be more appropriate ?
noted the TT earth label
wallywombat:
So if I'm interpreting that photo correctly, the DNO earthing facility is completely unused, and the amour of the 100m SWA cable is earthed at the load end to an earth rod?
If it was me I would change it so that that the armour is connected to the DNO earth at the feed end and isolated at the load end.
DNO earthing is unused.
Armour of SWA cable is currently connected at both ends i believe, but earthed via the earth rod at the load end.