AJJewsbury:AJJewsbury:RCD in the DNO cabinet would be the better solution since the clearance time for a earth fault may be above 5s
Provided everything is OK for voltage drop and R2 isn't massively larger than R1, I would be surprised if you couldn't get 5s disconnection times from the usual overcurrent protective devices.
- Andy.Come to that what is your voltage drop like? 100m is quite long for a LV submain and your diagram seems to suggest it's just 35mm² - on what's presumably something close to a 100A/phase system? While the tabulated v.d. of 1.1mV/A/m will be an over estimate as you'll be running the cable a bit cooler than 70 degrees there doesn't feel to be much scope for achieving the usual 3% overall for downstream lighting circuits - even an overall 5% to the end of final circuits looks rather tight (even if you claim the extra 0.005%/m beyond 100m).
- Andy.
Hi Andy,
As previously stated, the feeder cable cannot change and the volt drop has always been a concern (especially lighting), But my calcs have provided confidence that the volt drop is within the limits, some oversized cables down the line have been used purely for the volt drop.
A load assessment and final circuit voltage readings are to be recorded on completion for this very fact.
Sparkingchip:
Would you bond a steel framed steel clad building?
There is no practical difference between that cabinet and a steel framed building clad with steel, apart from the scale of them.
You can walk into a building, whilst you can only get your head and shoulders into the cabinet, but the risks are the same, if not higher with the cabinet.
So are you saying bond the cabinet to the PME, TT or leave the cabinet as is ? noting that the steel running from the cabinet into the conc plinth is probably in close contact if not connected to the TX/cutout earth electrode?
Would you bond a steel framed steel clad building? There is no practical difference between that cabinet and a steel framed building clad with steel, apart from the scale of them. You can walk into a building, whilst you can only get your head and shoulders into the cabinet, but the risks are the same, if not higher with the cabinet.
3. Don't bond the cabinet and in effect the cabinet floats at or close to the PME earth potential and so potentially have the same problem as point 2 above.