Multiple Earth Electrodes TT System

Thoughts or suggestions welcome....


Is there any issue or downside to having multiple earth electrodes installed on a single TT system (all areas have there CPC connected together) when the TT system spans a large area (we are taking about a 400m x 400m area)?


For example


If you had a couple of farm barns/sheds (metal framed) close together with multiple earth electrodes and some few hundred meters away you have a camp site with multiple earth electrodes (one at each power outlet etc) and then connect the CPC from the barns to the camp site to make one large TT system?



Parents
  • In general multiple electrodes would be considered a good thing - as generally a lower overall Zs and likely more reliable too.


    The only flipside I can think of is that having one large TT system rather than several small ones is that the rise PE potential during a L-PE fault will affect a larger area. Normally that's not too much of a concern but could be significant, say if an RCD was faulty and so failed to disconnect at all.


       - Andy.
Reply
  • In general multiple electrodes would be considered a good thing - as generally a lower overall Zs and likely more reliable too.


    The only flipside I can think of is that having one large TT system rather than several small ones is that the rise PE potential during a L-PE fault will affect a larger area. Normally that's not too much of a concern but could be significant, say if an RCD was faulty and so failed to disconnect at all.


       - Andy.