If you're using the supplier's earthing facility it'll certainly be TN. (I'd be surprised if it was really TN-S these days (unless it was an odd situation like a caravan site or a marina) - most DNOs seem pretty wedded to TN-C-S these days, even combining N and PE in modification to what were originally TN-S networks, effectively making them TN-C-S even though they appear for all the world to be TN-S at the cut-out.)
Cheers Andy. Spot on! I've just double checked the SPNetwork invoice and it is 40kVA TN-C-S. It's for a Nano/Micro Brewery. I'm hoping to do a fair amount of the install myself and get a qualified sparky to connect tails, check and test before operation.
If you're using the supplier's earthing facility it'll certainly be TN. (I'd be surprised if it was really TN-S these days (unless it was an odd situation like a caravan site or a marina) - most DNOs seem pretty wedded to TN-C-S these days, even combining N and PE in modification to what were originally TN-S networks, effectively making them TN-C-S even though they appear for all the world to be TN-S at the cut-out.)
Cheers Andy. Spot on! I've just double checked the SPNetwork invoice and it is 40kVA TN-C-S. It's for a Nano/Micro Brewery. I'm hoping to do a fair amount of the install myself and get a qualified sparky to connect tails, check and test before operation.