I'm trying to decide which would be the most suitable and sensible option?
I have a Control Board that will be switching 4x 3-Phase Immersion Elements.
9kW
9kW
6kW
3kW
Control Board has Rail Mount Fuse Holders & Contactors installed for each circuit.
My question is would it be better to have a suitably rated RCBO installed in the Distribution Board which will be feeding the Control Board or should I go with downstream Isolators with RCD's? I'm leaning towards the later as I would have separate RCD protection on each circuit.
Look forward to your feedback. Cheers, Dan.