Ze & Ipscc

I am preparing an electrical model for a project and have asked ukpn to confirm the Ze, Ipscc and Z% of the transformer so I can input the data in the software.


I got the following figures back which I am not sure I understand:

Ze=0.15

Ipscc=32kA

Z for the 11kV/400V 1.5MVA Tx 5.5%


Based on the Tx Z and Ipscc I would expect a much lower Ze. Am I missing something or do you think that the above figures make sense?
Parents
  • As Andy has said I also think that UKPN has given you worst case generic data.


    If that is realey the size and rating of the transformer then you can calculate PFC and Ze.
Reply
  • As Andy has said I also think that UKPN has given you worst case generic data.


    If that is realey the size and rating of the transformer then you can calculate PFC and Ze.