This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Ze & Ipscc

I am preparing an electrical model for a project and have asked ukpn to confirm the Ze, Ipscc and Z% of the transformer so I can input the data in the software.


I got the following figures back which I am not sure I understand:

Ze=0.15

Ipscc=32kA

Z for the 11kV/400V 1.5MVA Tx 5.5%


Based on the Tx Z and Ipscc I would expect a much lower Ze. Am I missing something or do you think that the above figures make sense?
Parents
  • As Andy has said I also think that UKPN has given you worst case generic data.


    If that is realey the size and rating of the transformer then you can calculate PFC and Ze.
Reply
  • As Andy has said I also think that UKPN has given you worst case generic data.


    If that is realey the size and rating of the transformer then you can calculate PFC and Ze.
Children
No Data