This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Is it correct 411.3.2.2

Max disconnection ...shall be applied to final circuits with a rated current not exceeding 

1. 63A with one or more socket-outlets, AND

2. 32 A supplying only fixed connected current-using equipment.


Example 32A with at least one socket with plugs.


condition 1 is satisfied

condition 2 is not satisfied


The “and” implies both need to be satisfied.


is this true? 


ian Bowie


Parents
  • I don't see what the problem is.


    The times in Table 411.1 shall apply to both types of circuit - hence 'and'.
Reply
  • I don't see what the problem is.


    The times in Table 411.1 shall apply to both types of circuit - hence 'and'.
Children
No Data