Is it correct 411.3.2.2

Max disconnection ...shall be applied to final circuits with a rated current not exceeding 

1. 63A with one or more socket-outlets, AND

2. 32 A supplying only fixed connected current-using equipment.


Example 32A with at least one socket with plugs.


condition 1 is satisfied

condition 2 is not satisfied


The “and” implies both need to be satisfied.


is this true? 


ian Bowie


Parents
  • At best the “and” is redundant  and would be better to have two lines in a list.


    while you can say that it’s not a logical statement - this is a scientific book and care should be exercised.


Reply
  • At best the “and” is redundant  and would be better to have two lines in a list.


    while you can say that it’s not a logical statement - this is a scientific book and care should be exercised.