Type A rcd . EICR coding ? etc

Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • My definition is quite simple, DC is a relatively constant voltage or current, which does not vary with time, in other words, a battery.

    Shades of the old "direct current" vs "continuous current" word war of yesteryear. I think the outcome was that d.c. could include ripple (i.e. could include a waveform, but overall it didn't cross zero - i.e. the polarity never alternated) while c.c. was your battery output. But the exact words don't matter as long as we userstand the meaning. Continuous current seem to be out of fashion these days so we have d.c. (sorry DC) and ripple-free DC.

    needs a manufacturer to describe how they think this is a problem

    I agree - there's still far too much confusion at the moment.


    So far it seems to me that there might be several different effects/symptoms/problems going on. There's the issue of DC saturating the coil and blinding the RCD to real faults (for which one fix seems to be a B-type RCD), But there also seems to be a separate issue of the fault current itself not being a complete a.c. waveform - e.g. a L-PE fault after a rectifier - which (allegedly) AC RCDs aren't guaranteed to be sensitive to. On a TN system I'd imagine that a L-PE short after a rectifier, if the RCD or OPD didn't disconnect, would blow the rectifier to smithereens in pretty short order and likely achieve some kind of disconnection fairly quickly anyway. On a TT system with potentially very low earth fault currents, it's seems possible that we'd end up with an uncleared fault. That I think is the sort of thing they're pushing A-type RCDs for.


       - Andy.
Reply
  • My definition is quite simple, DC is a relatively constant voltage or current, which does not vary with time, in other words, a battery.

    Shades of the old "direct current" vs "continuous current" word war of yesteryear. I think the outcome was that d.c. could include ripple (i.e. could include a waveform, but overall it didn't cross zero - i.e. the polarity never alternated) while c.c. was your battery output. But the exact words don't matter as long as we userstand the meaning. Continuous current seem to be out of fashion these days so we have d.c. (sorry DC) and ripple-free DC.

    needs a manufacturer to describe how they think this is a problem

    I agree - there's still far too much confusion at the moment.


    So far it seems to me that there might be several different effects/symptoms/problems going on. There's the issue of DC saturating the coil and blinding the RCD to real faults (for which one fix seems to be a B-type RCD), But there also seems to be a separate issue of the fault current itself not being a complete a.c. waveform - e.g. a L-PE fault after a rectifier - which (allegedly) AC RCDs aren't guaranteed to be sensitive to. On a TN system I'd imagine that a L-PE short after a rectifier, if the RCD or OPD didn't disconnect, would blow the rectifier to smithereens in pretty short order and likely achieve some kind of disconnection fairly quickly anyway. On a TT system with potentially very low earth fault currents, it's seems possible that we'd end up with an uncleared fault. That I think is the sort of thing they're pushing A-type RCDs for.


       - Andy.