Type A rcd . EICR coding ? etc

Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • How the fixed wiring is carried out is nothing to do with the boiler manufacturer. If they wish to remind the installing electrician of the Wiring Regulations they should say refer to BS7671. You may provide additional protection to the wiring with a type AC perfectly satisfactorily, can you get a DC current from the fixed wiring? Certainly NOT!  Do they give notes on the temperature rating of the cables, and instructions to not tie them to the hot pipes? I wonder why that is?
Reply
  • How the fixed wiring is carried out is nothing to do with the boiler manufacturer. If they wish to remind the installing electrician of the Wiring Regulations they should say refer to BS7671. You may provide additional protection to the wiring with a type AC perfectly satisfactorily, can you get a DC current from the fixed wiring? Certainly NOT!  Do they give notes on the temperature rating of the cables, and instructions to not tie them to the hot pipes? I wonder why that is?