AJJewsbury:
What about the fixed wiring after the boiler - e.g. between the boiler PCB and room 'stats and so on? - if that's concealed in a wall (it usually is) then BS 7671 will likely require additional protection by 30mA RCD - can we be sure that that wiring isn't fed by semiconductors?
- Andy.
But it could be a fault in the boiler as well ...
We can't go assuming the manufacturer has got it wrong just because it means the job is a little more difficult.
Engineering truism - Assumption is the mother of all muckups!
AJJewsbury:
What about the fixed wiring after the boiler - e.g. between the boiler PCB and room 'stats and so on? - if that's concealed in a wall (it usually is) then BS 7671 will likely require additional protection by 30mA RCD - can we be sure that that wiring isn't fed by semiconductors?
- Andy.
But it could be a fault in the boiler as well ...
We can't go assuming the manufacturer has got it wrong just because it means the job is a little more difficult.
Engineering truism - Assumption is the mother of all muckups!