Type A rcd . EICR coding ? etc

Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • Looking at the Worcester 2000 combi, the MIs state " the correct type of RCD must be employed where additional protection is required that is suitable for a low energy DC modulating pump according to IET wiring regulations"

    So it seems they are more worried about the pump.

    The manufacturers' external controls use extra low voltage DC via a bus.

    Also most modern boilers use flame rectification to prove the gas is burning, which puts a DC voltage to earth.

    So a lot of DC flying about.
Reply
  • Looking at the Worcester 2000 combi, the MIs state " the correct type of RCD must be employed where additional protection is required that is suitable for a low energy DC modulating pump according to IET wiring regulations"

    So it seems they are more worried about the pump.

    The manufacturers' external controls use extra low voltage DC via a bus.

    Also most modern boilers use flame rectification to prove the gas is burning, which puts a DC voltage to earth.

    So a lot of DC flying about.