Type A rcd . EICR coding ? etc

Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • After this thread, I wouldn't install a CU with type AC RCDs: that's the learning point. So you might ask whether Schneider appreciate the difficulty and why they continue to make these boards for the UK market. ?


    The other issue is the plumbers! In fact, they are v. old school and have done excellent work; but when they specify this particular Worcester boiler, which may be the most reliable kit available, do they know about the electrical implications? No!
Reply
  • After this thread, I wouldn't install a CU with type AC RCDs: that's the learning point. So you might ask whether Schneider appreciate the difficulty and why they continue to make these boards for the UK market. ?


    The other issue is the plumbers! In fact, they are v. old school and have done excellent work; but when they specify this particular Worcester boiler, which may be the most reliable kit available, do they know about the electrical implications? No!