Type A rcd . EICR coding ? etc

Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • AJJewsbury:

    I've been pondering the mention of additional/supplementary protection - presumably against direct contact - so we're expecting the RCD to see a residual current that's just flowing though a person who I presume is a fair approximation to a simple resistor so we shouldn't expect any waveform distortion or d.c. components on that score - so in that respect AC type RCDs should be adequate. On the other hand we have a load that might draw distorted waveform current for its normal load - so the RCD will see distorted a.c. load current plus pure sinewave shock current flowing out in its L coil, and just the distorted N return (without the shock current) in its N coil - so the question is: can we be sure that all AC type RCDs can spot a pure sinewave residual current when both the L and N load currents equally are distorted? I.e. does the insensitivity to distorted sinewaves occur before or after summing in the toroid?


    That is a pretty fair summary. In other words, might a fault in the boiler "blind" a type AC RCD?


    The manufacturer's instructions don't require that this particular boiler be RCD protected so in a TN installation, ADS should provide shock protection for a fault inside it. Whether or not a distorted load current would trip a type AC RCD becomes irrelevant. So that leaves a fault in the supply cable (which need not require additional protection) or in the many cables which control the heating system, which are buried in walls < 50 mm from the surface, and which I assume are at mains voltage.


    So to my mind, it is all about blinding. I await a response from the manufacturer.


Reply
  • AJJewsbury:

    I've been pondering the mention of additional/supplementary protection - presumably against direct contact - so we're expecting the RCD to see a residual current that's just flowing though a person who I presume is a fair approximation to a simple resistor so we shouldn't expect any waveform distortion or d.c. components on that score - so in that respect AC type RCDs should be adequate. On the other hand we have a load that might draw distorted waveform current for its normal load - so the RCD will see distorted a.c. load current plus pure sinewave shock current flowing out in its L coil, and just the distorted N return (without the shock current) in its N coil - so the question is: can we be sure that all AC type RCDs can spot a pure sinewave residual current when both the L and N load currents equally are distorted? I.e. does the insensitivity to distorted sinewaves occur before or after summing in the toroid?


    That is a pretty fair summary. In other words, might a fault in the boiler "blind" a type AC RCD?


    The manufacturer's instructions don't require that this particular boiler be RCD protected so in a TN installation, ADS should provide shock protection for a fault inside it. Whether or not a distorted load current would trip a type AC RCD becomes irrelevant. So that leaves a fault in the supply cable (which need not require additional protection) or in the many cables which control the heating system, which are buried in walls < 50 mm from the surface, and which I assume are at mains voltage.


    So to my mind, it is all about blinding. I await a response from the manufacturer.