AJJewsbury:
I think the worry about additional protection is that the boiler could remove additional protection from everywhere downstream of the RCD - so picture nail into a cable upstream of the boiler (or elsewhere in the house if the RCCB is covering many circuits) and additional protection might be ineffective.
I see three issues:
(1) The boiler, or at least it's DC modulating pump will trip a type AC RCD in normal use. I assume the electronics are rather like the front half of a VSD, so that is perfectly possible. That would be obvious during commissioning.
(2) A fault in the boiler might not trip a type AC RCD. I think that we have covered that one. If the boiler does not require RCD protection, then this possibility isn't a problem.
(3) The boiler might blind an RCD, either in normal use, or under some fault condition which does not trigger ADS.
I have asked Schneider whether their type AC RCDs are compatible with DC modulating pumps and I have asked Worcester to explain - i.e. to answer my original question.
All this does seem to be a bit beyond the call of duty. Perhaps the householder should have told the plumber to fit a boiler which can cope with a type AC RCD? ?
AJJewsbury:
I think the worry about additional protection is that the boiler could remove additional protection from everywhere downstream of the RCD - so picture nail into a cable upstream of the boiler (or elsewhere in the house if the RCCB is covering many circuits) and additional protection might be ineffective.
I see three issues:
(1) The boiler, or at least it's DC modulating pump will trip a type AC RCD in normal use. I assume the electronics are rather like the front half of a VSD, so that is perfectly possible. That would be obvious during commissioning.
(2) A fault in the boiler might not trip a type AC RCD. I think that we have covered that one. If the boiler does not require RCD protection, then this possibility isn't a problem.
(3) The boiler might blind an RCD, either in normal use, or under some fault condition which does not trigger ADS.
I have asked Schneider whether their type AC RCDs are compatible with DC modulating pumps and I have asked Worcester to explain - i.e. to answer my original question.
All this does seem to be a bit beyond the call of duty. Perhaps the householder should have told the plumber to fit a boiler which can cope with a type AC RCD? ?