Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • How do I select the correct Type of RCD?



    It is important to select the correct Type of RCD for the equipment to be used. The Type of RCD will depend on the characteristics of the equipment. Where necessary, equipment manufacturers should specify the RCD Type required. If the information is not available, the manufacturer should be contacted and asked to provide it. It is a legal requirement of UK Product Safety Regulations for manufacturers to provide clear installation instructions to enable safe installation.

    https://electrical.theiet.org/wiring-matters/years/2019/77-september-2019/which-rcd-type/


    It appears that Worcester Bosch are saying ask the IET and the IET are saying ask Worcester Bosch.

     


Reply
  • How do I select the correct Type of RCD?



    It is important to select the correct Type of RCD for the equipment to be used. The Type of RCD will depend on the characteristics of the equipment. Where necessary, equipment manufacturers should specify the RCD Type required. If the information is not available, the manufacturer should be contacted and asked to provide it. It is a legal requirement of UK Product Safety Regulations for manufacturers to provide clear installation instructions to enable safe installation.

    https://electrical.theiet.org/wiring-matters/years/2019/77-september-2019/which-rcd-type/


    It appears that Worcester Bosch are saying ask the IET and the IET are saying ask Worcester Bosch.

     