jcm:
EICR ,how do you know what type of RCD is fitted if not stated , I have one or two spare no markings as to what type they are. Can we give a code for that.
Now even 13amp socket outlets with one or two USB type A charging points are out of date , you now need sockets with USB charging points Type C . You can buy outlets with one Type C and one type A, witch covers both charging leads ,but of course more money and bother for customer to change existing ones.
The whole regulations are getting out of hand.
jcm
RCDs with no markings would normally be Type AC, and manufactured before RCD Types were introduced in the standards.
If the RCD is newer than that, then I don't believe it complies with no markings.
The RCD markings are:
IEC 60417 Symbol |
Type AC |
![]() |
Type A |
![]() |
Type F |
![]() |
Type B |
![]() or ![]() or ![]() |
jcm:
EICR ,how do you know what type of RCD is fitted if not stated , I have one or two spare no markings as to what type they are. Can we give a code for that.
Now even 13amp socket outlets with one or two USB type A charging points are out of date , you now need sockets with USB charging points Type C . You can buy outlets with one Type C and one type A, witch covers both charging leads ,but of course more money and bother for customer to change existing ones.
The whole regulations are getting out of hand.
jcm
RCDs with no markings would normally be Type AC, and manufactured before RCD Types were introduced in the standards.
If the RCD is newer than that, then I don't believe it complies with no markings.
The RCD markings are:
IEC 60417 Symbol |
Type AC |
![]() |
Type A |
![]() |
Type F |
![]() |
Type B |
![]() or ![]() or ![]() |