Type A rcd . EICR coding ? etc

Hi Guys.   Not been on for a long time, just had a bit of a search and couldn't really find anything so thought i would ask and see what you all thought.


1.  Are we or will we be coding type AC rcd's if there are LED's or induction hobs, lots of electronics  etc  present.

2. How much DC leakage does it actually take to saturate an rcd and cause  problem?

3. How much does a standard LED lamp or induction hob  leak ?

If we test an AC RCD with no load and it's fine then re-test it with all LED lights, induction hobs etc turned on and it operates correctly could we then say that it is ok with a note on EICR  OR EIC if installing any of the above.  


Obviously also on an EICR if the RCD then doesn't operate with it all on it becomes a C2 ?


Any thoughts



Gary
Parents
  • Chris Pearson:


    This is the reply:


    Thank you for the enquiry effectively you are looking for an A Type RCD which features the characteristics of a smooth DC fault current is less than 6 mA, as the standard RCDs we offer in this range as all AC type and dont have this feature,


    Why do Schneider mention smooth DC when a type A detects pulsating DC? Do they know their As from their elbows?


Reply
  • Chris Pearson:


    This is the reply:


    Thank you for the enquiry effectively you are looking for an A Type RCD which features the characteristics of a smooth DC fault current is less than 6 mA, as the standard RCDs we offer in this range as all AC type and dont have this feature,


    Why do Schneider mention smooth DC when a type A detects pulsating DC? Do they know their As from their elbows?