Isolation Transformer Control Circuit

Hello, I have been carrying out an EICR on an industrial installation and it was brought to my attention a control circuit at a machine has been supplied from a 230V Isolation transformer.  The transformer has no Neutral to Earth bond on the secondary side, the controls enclosures are metal clad with all exposed metal parts earth bonded back to the main earthing system on the primary side. There are several simultaneous conducting parts adjacent i.e. sockets, FSU, wall heater, structural steel support to building all adjacent to the console and it is conceivable that all conducting parts could easily be reached so a non-conducting location is not possible. 


My understanding of control circuits is that the common 0V connection must be grounded for several reasons, single fault detection and to ensure correct operation of contactors, relays, coils etc in the event of a single fault so as to mitigate maloperation.


Can anyone provide any advice/feedback please.


Cheers.



Parents
  • davezawadi (David Stone):

    This is quite normal. For a circuit with no access, one cannot receive a shock, and the control circuit probably controls contactors. Even if one side is Earthed, does this make the circuit safer? The answer is no, and 2 faults are required to make any risk, even if contact were possible.


    Correct regarding protection against electric shock. But it's not just about protection against electric shock, and not always normal for machinery controls.


    In general, BS EN 60204-1 control panels would use PELV for controls, to help faults in control wiring to show up ... for safety and business continuity reasons of course. This is due to the fact that for safety, digital control output signals are "sourcing" (switched from the "+" conductor) in negative-earth DC controls, or non-neutral AC conductor. Where, in odd circumstances, positive earthing is used for DC controls, the digital control output signals would be "sinking" (Switched from the "-" conductor) for the same reasons, but this is quite rare.


    Unless there's a good reason, PELV should be used in preference to SELV.


    Clause 6.1 of BS EN 60204-1 clearly says this (my highlight):



    6.1 General

    The electrical equipment shall provide protection of persons against electric shock by:

    – basic protection (see 6.2 and 6.4), and;

    – fault protection (see 6.3 and 6.4).

    The measures for protection given in 6.2, 6.3, and, for PELV, in 6.4, are a selection from

    IEC 60364-4-41. Where those measures are not practicable, for example due to the physical

    or operational conditions, other measures from IEC 60364-4-41 may be used (e.g. SELV)
    .


    So, I'm not saying SELV is definitely wrong in this case (SELV is necessarily used for some physical communications circuits, such as Ethernet, for example, which are used for control). However, it depends on whether PELV was practicable for the particular circuit or application, and more importantly whether there would be a controls safety issue if a fault in the control wiring were not detected ... the understanding the OP has, that PELV is normally used for controls in machinery, is 100 % correct.
Reply
  • davezawadi (David Stone):

    This is quite normal. For a circuit with no access, one cannot receive a shock, and the control circuit probably controls contactors. Even if one side is Earthed, does this make the circuit safer? The answer is no, and 2 faults are required to make any risk, even if contact were possible.


    Correct regarding protection against electric shock. But it's not just about protection against electric shock, and not always normal for machinery controls.


    In general, BS EN 60204-1 control panels would use PELV for controls, to help faults in control wiring to show up ... for safety and business continuity reasons of course. This is due to the fact that for safety, digital control output signals are "sourcing" (switched from the "+" conductor) in negative-earth DC controls, or non-neutral AC conductor. Where, in odd circumstances, positive earthing is used for DC controls, the digital control output signals would be "sinking" (Switched from the "-" conductor) for the same reasons, but this is quite rare.


    Unless there's a good reason, PELV should be used in preference to SELV.


    Clause 6.1 of BS EN 60204-1 clearly says this (my highlight):



    6.1 General

    The electrical equipment shall provide protection of persons against electric shock by:

    – basic protection (see 6.2 and 6.4), and;

    – fault protection (see 6.3 and 6.4).

    The measures for protection given in 6.2, 6.3, and, for PELV, in 6.4, are a selection from

    IEC 60364-4-41. Where those measures are not practicable, for example due to the physical

    or operational conditions, other measures from IEC 60364-4-41 may be used (e.g. SELV)
    .


    So, I'm not saying SELV is definitely wrong in this case (SELV is necessarily used for some physical communications circuits, such as Ethernet, for example, which are used for control). However, it depends on whether PELV was practicable for the particular circuit or application, and more importantly whether there would be a controls safety issue if a fault in the control wiring were not detected ... the understanding the OP has, that PELV is normally used for controls in machinery, is 100 % correct.