gkenyon:
So, you take Zs before the inverter (dimmer switch or electronic switch) and R1+R2 downstream.
An interesting topic, but a bit too technical for me!
However, I was thinking about the location of a VSD. If it is built into a machine, i.e. when you pick up the machine, the VSD comes too, then clearly it is not part of the fixed wiring.
If it supplies something which is part of the fabric of the building, let's say HVAC apparatus, the fixed wiring probably goes as far as the pumps or fans, etc.
It it sits on the wall adjacent to a machine, the boundary really is rather vague. Presumably it would be specified in any EICR.
gkenyon:
So, you take Zs before the inverter (dimmer switch or electronic switch) and R1+R2 downstream.
An interesting topic, but a bit too technical for me!
However, I was thinking about the location of a VSD. If it is built into a machine, i.e. when you pick up the machine, the VSD comes too, then clearly it is not part of the fixed wiring.
If it supplies something which is part of the fabric of the building, let's say HVAC apparatus, the fixed wiring probably goes as far as the pumps or fans, etc.
It it sits on the wall adjacent to a machine, the boundary really is rather vague. Presumably it would be specified in any EICR.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site