ZS for an motor run off an inverter

Hi guys. How can you test the zs of a motor run off an inverter drive?
Parents
  • lyledunn:
    gkenyon:

    Yes, application of Regulation 419.3 is feasible, and then the question of a loop impedance disappears.


    Yes unless you want to argue that the prospective earth fault current should be assessed.




    Loop impedance is only required for ADS.


    The prospective fault current is required for a number of things ... ADS, if it applies in a particular arrangement, is only one possibility ...


Reply
  • lyledunn:
    gkenyon:

    Yes, application of Regulation 419.3 is feasible, and then the question of a loop impedance disappears.


    Yes unless you want to argue that the prospective earth fault current should be assessed.




    Loop impedance is only required for ADS.


    The prospective fault current is required for a number of things ... ADS, if it applies in a particular arrangement, is only one possibility ...