Help wanted to read/understand an electrical supply plan from DNO - updated new query

EDIT: I have one further query: WPD say that if they were upgrading the local network they would overlay the current 95mm wcon cable with a 185mm wcon cable, but that this alone would not be sufficient to allow for my property to be connected to the local network. Instead, they said that for me to be connected, a 300mm wcon cable needs to be laid, and they want me to fund the difference between the 185 cable and the 300 cable. 


As they were less than scrupulously transparent in their previous quote, I would like to check if anybody has any thoughts on the veracity of this? Why would upgrading to a 185mm cable not allow sufficient capacity to add my supply?




Original question (already answered):Can anybody assist me in understanding what an existing plan provided by my DNO is showing, and what this means for my request for a new supply please? I've had a very large quote to connect our new house (a passive house) to the network, and am not certain that it is quite right. It appears to be asking us to upgrade the local supply from a 95mm2 cable to a 300mm2 cable, and I am being asked to pay 70% of the cost of that. I was told that if this isn't done, the lights would go out for the rest of the street. I'm not an electrical engineer, so am looking for knowledge with which to go back and discuss the quote. Thanks!



Plan of existing supply.pdf


Plan of proposed new supply.pdf
  • perspicaciousAlcomaxstattermapj1‍ and others, just to say a huge thank you all - I've now received a revised quote from WPD for around £3k which is a massive improvement!

    I haven't actually spoken to the chap there yet, but he clearly took on board the content of my email about the upgrade being the company's responsibility, and the fact that they were going to need to do that anyway when everyone has an electric vehicle.


    The proposed scheme remains the same in terms of running the new cable to the pole and then connecting us up, rather than running a cable directly to us from the Tx, but I am no longer being asked to pay for all that.


    You are all absolute heroes and heroines. Thank you so much!!

    Morgan


  • That is good news - sounds like they have agreed you have to pay only much as if you had had  your own private connection line direct to the TX, but they do need the upgrade anyway,  and  they dig into their own reserves to fund the rest of it that is not benefiting you. It does make me wonder rather how often stuff like that just gets waved through un-noticed. Maybe quite often if no-one queries it.


    It is always nice to know how things pan out - often folk just vanish and we are not sure what has happened.

    Do come back as and when there are further queries..

    best regards Mike.
  • Glad to hear that.  £3k is much more reasonable.  Do share your experience with the WPD  Customer Experience Group.  They will be looking at connections and WPD plans for the next reg period which should include tightening up on this sort of thing.


  • Former Community Member
    0 Former Community Member
    What was the original quoted price before they phoned a manager to get you a discount?
  • Weirdbeard:

    What was the original quoted price before they phoned a manager to get you a discount?


    £14,000


  • Are you fitting the electrical installation? The members will need to be warned!

    Regards, UKPN
  • I wonder if you referenced this discussion to them, if so then Great! You might do the same to the experience group.


    Kind regards

    David CEng Etc.