Chris Pearson:Nano Brewery:Chris Pearson:
Could you not have an RCD incomer in the DB?Cheers Chris. I was hoping to keep all elements on separate circuits, and also have RCDs on all circuits, just so if one develops a fault the other 3 will continue to operate, and any fault will be quicker and easier to detect?
No, I wouldn't look at it that way. Each element will have its own MCB/fuse. A short circuit would trip the MCB, but not the RCD. A fault (i.e. to earth) might trip both. Ok, that is a bit of a bother if the whole lot goes off. I am not sure how that affects your business, but if it slows down a batch, is that an issue? If it occurred, you can still isolate the faulty element by its MCB.
Cheers Chris. With this in mind, maybe the option of an RCD to MCB (or an RCBO) in the Distribution Board, then feeding out to the Control Panel would be the way to go? It would then just be the Control Panel (Elements) that would go out in the event of an Earth fault and not the whole place?
...Would I even require an MCB in the Distribution Board for the Control Panel feed, or could I just feed direct from the RCD? At present the Control Panel has 6 individual circuits, with Rail Mounted Cartridge Fuses and Contactors installed on each.
Chris Pearson:Nano Brewery:Chris Pearson:
Could you not have an RCD incomer in the DB?Cheers Chris. I was hoping to keep all elements on separate circuits, and also have RCDs on all circuits, just so if one develops a fault the other 3 will continue to operate, and any fault will be quicker and easier to detect?
No, I wouldn't look at it that way. Each element will have its own MCB/fuse. A short circuit would trip the MCB, but not the RCD. A fault (i.e. to earth) might trip both. Ok, that is a bit of a bother if the whole lot goes off. I am not sure how that affects your business, but if it slows down a batch, is that an issue? If it occurred, you can still isolate the faulty element by its MCB.
Cheers Chris. With this in mind, maybe the option of an RCD to MCB (or an RCBO) in the Distribution Board, then feeding out to the Control Panel would be the way to go? It would then just be the Control Panel (Elements) that would go out in the event of an Earth fault and not the whole place?
...Would I even require an MCB in the Distribution Board for the Control Panel feed, or could I just feed direct from the RCD? At present the Control Panel has 6 individual circuits, with Rail Mounted Cartridge Fuses and Contactors installed on each.