AJJewsbury:
We've got I think a total of 27kW - so at least 40A/phase - as I've not seen any 3-phase RCBOs rated that high yet (usually 32A max) I suspected that an upstream RCBO might not have been intended.
So can we agree that RCD protection is not required? I must say that I don't see any requirement for it as far as this circuit is concerned.
AJJewsbury:
We've got I think a total of 27kW - so at least 40A/phase - as I've not seen any 3-phase RCBOs rated that high yet (usually 32A max) I suspected that an upstream RCBO might not have been intended.
So can we agree that RCD protection is not required? I must say that I don't see any requirement for it as far as this circuit is concerned.