Are RCD's Required?

Hi, looking to understand if an RCD would be a required regulation (and/or just highly recommended) in the following situation.  The additional cost of installing four or five 3-Phase RCDs is quite substantial and I would prefer to avoid it if still deemed as safe and not legally required.  Earthing system is TN-C-S.


For connecting up 4x Immersion Elements (9kW, 9kW, 6kW, 3kW) in Brewery Tanks I am looking at either:


A.  SWA Cable clipped direct to basket from the Control Panel to IP rated Plugs/Sockets mounted on the wall.  Then floating SY Cable (recommended by electrician) from the wall to the Tanks, which is about a 2m run.  Thinking Plugs/Sockets just to make life easy if I ever want to move things around and also for easier access for cleaning.


B.  Same as above but swapping the Plugs/Sockets for Isolators.


Look forward to your feedback and opinions.  Cheers.
Parents
  • though without having socket outlet it is better to have RCD   then if cable damage by accidently connect with metal structure  power will goes off  without harm  to any thing ,,MCB or fuse is activate by presser high current
Reply
  • though without having socket outlet it is better to have RCD   then if cable damage by accidently connect with metal structure  power will goes off  without harm  to any thing ,,MCB or fuse is activate by presser high current