Hi, looking to understand if an RCD would be a required regulation (and/or just highly recommended) in the following situation.  The additional cost of installing four or five 3-Phase RCDs is quite substantial and I would prefer to avoid it if still deemed as safe and not legally required.  Earthing system is TN-C-S.


For connecting up 4x Immersion Elements (9kW, 9kW, 6kW, 3kW) in Brewery Tanks I am looking at either:


A.  SWA Cable clipped direct to basket from the Control Panel to IP rated Plugs/Sockets mounted on the wall.  Then floating SY Cable (recommended by electrician) from the wall to the Tanks, which is about a 2m run.  Thinking Plugs/Sockets just to make life easy if I ever want to move things around and also for easier access for cleaning.


B.  Same as above but swapping the Plugs/Sockets for Isolators.


Look forward to your feedback and opinions.  Cheers.
Parents
  • AJJewsbury:
    Wondering if a direct feed from a Distribution Board RCD to the Control Panel could be an option for universal protection at less cost? Is this possible and allowed? Alternatively, maybe Tails split via a Henley Box >>> RCD (stand alone) >>> Control Panel?

    Definitely not tails to RCD to control panel - you'd need some circuit overcurrent protection in there.




    Cheers Andy. 


    Even with the Control Panel having Cartridge Fuses installed on each circuit?  I thought these would be providing the Overcurrent Protection? 


    The main issue seems to be that the 4 Three-phase Immersion Elements (which will be switched via the Control Panel) will be pulling 33kW (48 Amps) when all 4 are switched on.  Too much for an RCBO feed direct from the Distribution Board.

    To update others - I'm just looking for the most cost effective solution for incorporating RCD protection for additional safety with there being lots of metal and liquids present.


Reply
  • AJJewsbury:
    Wondering if a direct feed from a Distribution Board RCD to the Control Panel could be an option for universal protection at less cost? Is this possible and allowed? Alternatively, maybe Tails split via a Henley Box >>> RCD (stand alone) >>> Control Panel?

    Definitely not tails to RCD to control panel - you'd need some circuit overcurrent protection in there.




    Cheers Andy. 


    Even with the Control Panel having Cartridge Fuses installed on each circuit?  I thought these would be providing the Overcurrent Protection? 


    The main issue seems to be that the 4 Three-phase Immersion Elements (which will be switched via the Control Panel) will be pulling 33kW (48 Amps) when all 4 are switched on.  Too much for an RCBO feed direct from the Distribution Board.