This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Kettles

Former Community Member
Former Community Member
OK 2nd question modern kettles with base power cord system instead of the older lead system but instead the docking system do I test the base separately or test them together as one itemModern kettle base
Parents
  • yes - but do actually look at them 'open' as well - damage to the base connectors is quite possible especially if it has got wet.

    Be aware that in many designs there are metal bits of the jug part that are  not earthed, by design,  only the element is, so you  may need to do a hybrid test, of either continuity from jug to CPC, or isolation at 500V  from jug to CPC, depending.
Reply
  • yes - but do actually look at them 'open' as well - damage to the base connectors is quite possible especially if it has got wet.

    Be aware that in many designs there are metal bits of the jug part that are  not earthed, by design,  only the element is, so you  may need to do a hybrid test, of either continuity from jug to CPC, or isolation at 500V  from jug to CPC, depending.
Children
No Data