gkenyon:Is that a safety issue?
I can, however, see that in hospitals, more attention is absolutely necessary with equipment that may be used in a Group 1 or Group 2 medical location - but I'd expect a greater degree of competence to test and maintain that equipment anyway?
In any case, even testing Class I appliances in that way won't always detect issues that cause RCDs to trip - or even detect all faults.
For example, if you test a washing machine, a faulty component or circuit may not be switched "on" until the door is closed and the interlock connects, and the component is in circuit set by the control board.
gkenyon:Is that a safety issue?
I can, however, see that in hospitals, more attention is absolutely necessary with equipment that may be used in a Group 1 or Group 2 medical location - but I'd expect a greater degree of competence to test and maintain that equipment anyway?
In any case, even testing Class I appliances in that way won't always detect issues that cause RCDs to trip - or even detect all faults.
For example, if you test a washing machine, a faulty component or circuit may not be switched "on" until the door is closed and the interlock connects, and the component is in circuit set by the control board.