Class 1 appliance with no exposed metal work to connect test lead too
Former Community Member
OK 3rd problem class one appliance with no exposed metal work to connect test lead too how can I carry out the earth bond test given it is a class 1 appliance and not a class 2 appliance like this
"It may only be the motor that's connected in a Class I configuration, for example, either for EMC purposes, or because of static."
I must admit that I have had to find testing points on some rotory floor cleaners that have lots of surface metal but without an obvious PE connect point.
"It may only be the motor that's connected in a Class I configuration, for example, either for EMC purposes, or because of static."
I must admit that I have had to find testing points on some rotory floor cleaners that have lots of surface metal but without an obvious PE connect point.