The Arc Fault Detection Device… again.

Some humourous but valid observations on AFDDs, the state of the industry, the wiring regs and future amendment requirements.

He also attempts to build a AFFD tester which electrically tests rather than relying upon the mechanical action of the test button on the device itself.

https://www.youtube.com/watch?v=e0ElFaKc_e8

Parents
  • Colin Jenkins:

    Hello Chris.

    It's something I picked up several years back when I was reading the specs and experience of AFDDS in the USA vs UK, but I must admit I can't find that first-hand now.

    AFDDs for sale in the UK must comply with BS EN 62606.  I haven't got access to that, but Schneider have a technical description of their AFDDs with respect to BS EN 62606 and this refers to the requirement that an AFDD must trip in 1 second at 2.5 amps.


    I asked because I think that the generation of myths should be avoided. BS EN 62606:2013+1 does not, as far as I can see, specify a threshold.


    Here is table 1 from the BS - maximum break time against test arc current


    2,5 A     5 A    10 A     16 A     32 A    63 A

     1,0 s  0,5 s  0,25 s  0,15 s  0,12 s  0.12 s


    That they must trip within 1.0 s at 2.5 A does not mean that do not at lower currents, but I think that one could infer that they need not do so. Certainly, I don't think that one could rely on them tripping significantly lower than 2.5 A.


    Interestingly Schneider say: "a series arc is dangerous as soon as its value equals or exceeds 2.5 Amps".


    It may be that a lighting circuit feeds only fixed luminaires whose total consumption is < 2.5 A in which case AFDD would be pointless; but as soon as you have lamp-holders, it would be difficult to be sure.


Reply
  • Colin Jenkins:

    Hello Chris.

    It's something I picked up several years back when I was reading the specs and experience of AFDDS in the USA vs UK, but I must admit I can't find that first-hand now.

    AFDDs for sale in the UK must comply with BS EN 62606.  I haven't got access to that, but Schneider have a technical description of their AFDDs with respect to BS EN 62606 and this refers to the requirement that an AFDD must trip in 1 second at 2.5 amps.


    I asked because I think that the generation of myths should be avoided. BS EN 62606:2013+1 does not, as far as I can see, specify a threshold.


    Here is table 1 from the BS - maximum break time against test arc current


    2,5 A     5 A    10 A     16 A     32 A    63 A

     1,0 s  0,5 s  0,25 s  0,15 s  0,12 s  0.12 s


    That they must trip within 1.0 s at 2.5 A does not mean that do not at lower currents, but I think that one could infer that they need not do so. Certainly, I don't think that one could rely on them tripping significantly lower than 2.5 A.


    Interestingly Schneider say: "a series arc is dangerous as soon as its value equals or exceeds 2.5 Amps".


    It may be that a lighting circuit feeds only fixed luminaires whose total consumption is < 2.5 A in which case AFDD would be pointless; but as soon as you have lamp-holders, it would be difficult to be sure.