The Arc Fault Detection Device… again.

Some humourous but valid observations on AFDDs, the state of the industry, the wiring regs and future amendment requirements.

He also attempts to build a AFFD tester which electrically tests rather than relying upon the mechanical action of the test button on the device itself.

https://www.youtube.com/watch?v=e0ElFaKc_e8

Parents
  • Colin Jenkins:

    Hello Chris.

    With my apologies, it looks like the no-trip threshold is 1.5 amps.  It's on page 6 of Wylex's AFDD/RCBO leaflet attached here.

    Regards,

                  Colin.         20200113123032_0_Wylex Single Module AFDD Cat Nov 19.pdf


    Colin, no need to apologise at all. At, say 2 A that Wylex device could spend many seconds, minutes or even hours thinking about whether to trip or not and still be in spec. To be honest, I hadn't realised that there is a threshold current for these devices.


    I am so tempted to do some experimentation JW-style, but I am far too mean to buy an AFDD. ?


Reply
  • Colin Jenkins:

    Hello Chris.

    With my apologies, it looks like the no-trip threshold is 1.5 amps.  It's on page 6 of Wylex's AFDD/RCBO leaflet attached here.

    Regards,

                  Colin.         20200113123032_0_Wylex Single Module AFDD Cat Nov 19.pdf


    Colin, no need to apologise at all. At, say 2 A that Wylex device could spend many seconds, minutes or even hours thinking about whether to trip or not and still be in spec. To be honest, I hadn't realised that there is a threshold current for these devices.


    I am so tempted to do some experimentation JW-style, but I am far too mean to buy an AFDD. ?