I don't see why not for smaller sizes provided that the cable is well clipped as the stuffing gland will be much less robust than a normal gland. I would also cut the armour back (I assume its not needed for CPC) to just outside the gland and cover the sheath, exposed armour and inner sheath with a thick heat shrink ideally adhesive lined. That way the stuffing gland wont force the armour into the sheath/ insulation. You will need to take special care with the way that the armour is cut to avoid jagged / bent ends which will cause more trouble than usual.
I don't see why not for smaller sizes provided that the cable is well clipped as the stuffing gland will be much less robust than a normal gland. I would also cut the armour back (I assume its not needed for CPC) to just outside the gland and cover the sheath, exposed armour and inner sheath with a thick heat shrink ideally adhesive lined. That way the stuffing gland wont force the armour into the sheath/ insulation. You will need to take special care with the way that the armour is cut to avoid jagged / bent ends which will cause more trouble than usual.