Bonding Question

Hi All


Hope you are well - just looking for a bit of guidance on bonding on a job - schematic picture attached.


Basically, 200A head to busbar chamber (TNCS)


63A SPN switch fuse to Building 1 - a big metal shed - 35mm buried SWA 3 core. For main bonding, I understand I have to put 35mm bonds to metalwork. Incoming pipes are plastic. Will I need to bond the incoming BT? Single copper line off the road.


200A isolator to central plant room - 185m away with a 200A MCCB board. This is to feed 5 buildings inc. a 3 phase. Plant room will have an MCB board also for external lighting and air con units which will serve 2 buildings via buried refrigerant pipe. Also a booster pump with metal pipework which is plastic as it leaves/enters the room. Also a central TV/radio system to feed coax out to the 5 buildings fed from here.


As I understand, I need to do 35mm bonds for structure, air con, and also BT incomer and aerial. Believe latter two to be 6mm? Also supplementary 2.5mm bonds for pipes, pumps, metal door frames.


All 5 properties fed from plant room have 35 or 50mm feeds and I understand these all need 35 main bonds for structure, AC pipes (where fed from ac outdoor units at plant room). For coax and BT cables - 6mm bonds? 


In a nutshell - am I correct in my understanding of the bonding sizes, in particular  telecoms and BT feeds? Using combined CPC and bonding conductors. I tend to see 6mm for comms and TV stuff.


A sanity check would be very welcome.


Regards


Muhammad

 
 

446fc18f3228f993e9ad6284b8d5108f-huge-schem.png
Parents
  • Thanks gents


    Mapj1 - pipes entering and exiting are plastic, metal is just in the room. 


    The water pipes are all plastic coming into or leaving buildings - only metal internal to the central plant room. 


    Andy


    I get where you are coming from - the 6mm is basically something I have seen on old drawings in various practices in the past. These used to show main bonds for everything else as the 54.8 sizes, but only with connections to TV/radio  and BT incoming distribution point being smaller at 6mm - presumably following the principle in Mapj1's post.


    For the outbuildings will be fibre for data and tv now anyway. Just copper coming into the central plant room


    Regards


    Muhammad

Reply
  • Thanks gents


    Mapj1 - pipes entering and exiting are plastic, metal is just in the room. 


    The water pipes are all plastic coming into or leaving buildings - only metal internal to the central plant room. 


    Andy


    I get where you are coming from - the 6mm is basically something I have seen on old drawings in various practices in the past. These used to show main bonds for everything else as the 54.8 sizes, but only with connections to TV/radio  and BT incoming distribution point being smaller at 6mm - presumably following the principle in Mapj1's post.


    For the outbuildings will be fibre for data and tv now anyway. Just copper coming into the central plant room


    Regards


    Muhammad